vinnymac44
Mechanical
- Jun 10, 2019
- 1
The project I am working on is a extra hazard group 1 occupancy and it includes one 14x14 overhead door. We will need to protect under the door as required.
NFPA 13 2010 edition 8.7.3.1.7 says that "where sidewall standard spray sprinklers are installed to protect areas below overhead doors within ordinary hazard occupancy spaces or rooms, protection area and maximum sprinkler spacing for light hazard as specified in table 8.7.2.2.1 shall be permitted under the overhead doors."
I need some insight on how to approach protecting under the door when it is open. Since 8.7.3.1.7 only references OH and not EH I am kinda stuck on the approach. We would like to stick to sidewalls if possible but I wanted to see if any one else has ran into this or if there is something else in NFPA 13 that I am missing.
NFPA 13 2010 edition 8.7.3.1.7 says that "where sidewall standard spray sprinklers are installed to protect areas below overhead doors within ordinary hazard occupancy spaces or rooms, protection area and maximum sprinkler spacing for light hazard as specified in table 8.7.2.2.1 shall be permitted under the overhead doors."
I need some insight on how to approach protecting under the door when it is open. Since 8.7.3.1.7 only references OH and not EH I am kinda stuck on the approach. We would like to stick to sidewalls if possible but I wanted to see if any one else has ran into this or if there is something else in NFPA 13 that I am missing.