Extra Loop for MV Cables

Jpascp

Electrical
Jan 15, 2025
8
Do you usually use in electrical installations extra loop for MV Cables in origin/from and destination/to?

1741026877793.png



I believe that is a good solution in case of an event short circuit at its terminals.
 
Replies continue below

Recommended for you

I have seen MV cables specified as a minimum length (In that case 100 Feet minimum) to limit the ASCC to the rating of the switchgear.
The extra cable was looped in the cable tray.
 
The image didn’t load for me, but looping cable in a vault means that when a termination or splice fails you still have cable to do it again without needing to splice in an extension. Termination/splice failures seem far more common than actual cable failures.
 