Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Extra Loop for MV Cables

Status
Not open for further replies.

Jpascp

Electrical
Joined
Jan 15, 2025
Messages
32
Do you usually use in electrical installations extra loop for MV Cables in origin/from and destination/to?

1741026877793.png



I believe that is a good solution in case of an event short circuit at its terminals.
 
I have seen MV cables specified as a minimum length (In that case 100 Feet minimum) to limit the ASCC to the rating of the switchgear.
The extra cable was looped in the cable tray.
 
The image didn’t load for me, but looping cable in a vault means that when a termination or splice fails you still have cable to do it again without needing to splice in an extension. Termination/splice failures seem far more common than actual cable failures.
 
Yes, a loop in each vault is typical practice in my region.
 
Yes, and in any pulling vaults between the to and from vaults.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top