farmape
Electrical
- Jan 16, 2008
- 50
Power logging at the 480V 3P 4W main panel (panel that feeds an outdoor lighting only load)
Consider a three phase 4 wire 480V circuit with the following average amperage (Fundamental) measurements:
L1: 191.5A, -7.84 deg
L2: 177.9A, -130.92 deg
L3: 178A, -253.02 deg
N: 20.6A, -156.9 deg
The actual phase RMS values for the circuit are nearly identical, except for Neutral which is about 65Amps RMS, over 300% higher than the fundamental!
THD values are:
L1: 11%
L2: 11%
L3: 12%
N: 280+%
Any thoughts on these excessive harmonics, is it even possible without some type of outside influence? The 3rd Harmonic is the culprit. Thanks
Consider a three phase 4 wire 480V circuit with the following average amperage (Fundamental) measurements:
L1: 191.5A, -7.84 deg
L2: 177.9A, -130.92 deg
L3: 178A, -253.02 deg
N: 20.6A, -156.9 deg
The actual phase RMS values for the circuit are nearly identical, except for Neutral which is about 65Amps RMS, over 300% higher than the fundamental!
THD values are:
L1: 11%
L2: 11%
L3: 12%
N: 280+%
Any thoughts on these excessive harmonics, is it even possible without some type of outside influence? The 3rd Harmonic is the culprit. Thanks