Dear all,
Has anyone used a trapezoidal wind load for a 6 m (20ft) facade in height? e.g. by calculating the wind load at 6 m and at the ground, and taking the trapezoidal load distribution... Is it allowed?
 
Replies continue below

Recommended for you

It is allowed in every wind code I've seen. Note that some wind codes have either a minimum magnitude design wind pressure or a minimum average wind pressure.

ASCE 7 even 'encourages' it by requiring the resultant force vector to be located at 55% of the height for certain structures (signs and freestanding walls)
 