lrohn
Electrical
- May 7, 2003
- 2
When checking equipment capacities and equipment utilization efficiencies at a recently acquired facility found that phase current to motors was unbalanced. e.g. 25 hp motor with phase current of 32,32, and 20 amps. This type of unbalance is at every motor ranging from 3hp to 100 hp. Power is provided thru 3- 500kva xfmrs connected delta primary and delta secondary with one phase grounded. Xfmr secondary and motor voltages are approx 459, 459 and 472 VAC which is 2.8% unbalance. Had the utility check their side and they say is ok. I checked the few small 1ph. lighting xfmrs and single ph. loads are fairly evenly divided. The distance to the elect rm equipment from the xfmrs is about 80 feet with wire lengths equal. Located the old electricial contractor that did work for the previous owners and they said they noticed problem never found a good solution or even the cause. They changed one of the 500 kva xfmrs but did not help. In effect just de-rated the motors and operated in that manner. They were eager to come in again and run up another bill. Any ideas or other suggestions of other things to look at?