Could you please mentioned the actual reason of the following false tripping of one healthy feeder due to a single line to ground fault on the adjacent feeder.
Details are as follows:
Both feeders are being fed from the same bus 33KV feeding each one one string of an offshore wind farm. They are adjacent to each other like feeder 1 and 2. Feeder 2 had SLG fault and it caused feeder 1 also tripped on the same time.

Faulty Feeder 2 : Offshore wind farm string with 7 turbines of 7MW each, 33 KV, total string cable length 10KM (Underground cable 3x1x800 Sq.mm CU/XLPE/STA/PVC), CT 1000/1 with Micom P139 relay.
Protection settings:
Protection_settings_qlqv0q.png


Healthy Feeder 1 which also tripped : Offshore wind farm string with 7 turbines of 7MW each, 33 KV, total string cable length 10KM (Underground cable 3x1x800 Sq.mm CU/XLPE/STA/PVC), CT 1000/1 with Micom P139 relay.
Protection settings:
Protection_settings_qlqv0q.png


To note that in another feeder it is connected a 315 kVA Y-Y earthing/auxiliary transformer with both neutral points directly earthed.

Could you please explain the actual reason and measures to be taken to avoid such false tripping. Could it be due to a sympathetic tripping event?
Best Regards.
 
Replies continue below

Recommended for you

Directional or non-directional overcurrent elements? If non-directional it's very likely that turbines on the non-faulted feeder supplied enough fault current that their feeder also tripped.
 
Feeders 1&2 both are source feeders. If the fault is in feeder-2, the fault current flows in to fault from the generators connected to feeder-1 to 33kV bus to fault in feeder-2.
So, the relays in both feeders see the fault. If the settings are identical (as it shows) and if the protection is non-directional (presumably), the protection in both feeders operate simultaneously and isolate both feeders.
Solution is to directionalise the protection. This applies to phase overcurrent protection as well.
 
Hi,

Thank for your replies.

If it is the case RRaghunath describes, why a third string feeder, Feeder 3, connected to the same 33 kV bus didn't had same behaviour than Feeder 1 and didn't trip?
 
I would expect Feeder-3 which is identical to feeder-1&2 also to trip.
The reasons for not tripping (though I am sure you are happy that it has not tripped) could be that the
[ul]
[li]contribution from that feeder was lower than the pickup threshold set in the protection (may be no. of generators working are less) or[/li]
[li]there is some problem with the relay (relay needs to be tested) or[/li]
[li]problem in the protection DC system in the feeder.[/li]
[/ul]
 