I've been looking at Equipment Schedules for Fan Coil Units. And I have some issues that I would be grateful if someone could clear up.
#1.
The Airflows in the Fan Coil Schedules are the ones that will actually occur in the zone based on the calculated ESP. However the SP stated in the schedule is (Total ESP). What is this Total ESP? (It's stated as 1 in.wg which seems quite high since most duct runs are 20-30 ft long for these FCUs, It's a private residence) What makes it more unclear is that this "Total ESP" is constant for all of the FCUs in the schedule regardless of their stated airflow and heat capacities.
What makes sense from my point of view is to state the calculated ESP in the schedule, since this would provide a more defined criteria for equipment selection by the contractor who will end up executing the project (i.e. I need an FCU that can provide X CFM at Y ESP).
#2. For small FCUs, there is no Fan Curve provided and what I have is FCU airflows at ESP increments of 0.05 in.wg. It is very unlikely that my calculated ESP will coincide with any one of these points exactly. The only solution I can think of is plotting these points and generating the fan curve myself.
On the other hand I am thinking that I'm trying to be too detailed since this is not exactly a critical application (as stated above, it's a residence). Is it acceptable if the eventual airflow upon installation deviates from the one stated in the schedule? As in, Equipment Schedules are guidelines for the contractors and not something that is to be executed precisely.
I apologize if my post is too long. Thank you.
Regards
I've been looking at Equipment Schedules for Fan Coil Units. And I have some issues that I would be grateful if someone could clear up.
#1.
The Airflows in the Fan Coil Schedules are the ones that will actually occur in the zone based on the calculated ESP. However the SP stated in the schedule is (Total ESP). What is this Total ESP? (It's stated as 1 in.wg which seems quite high since most duct runs are 20-30 ft long for these FCUs, It's a private residence) What makes it more unclear is that this "Total ESP" is constant for all of the FCUs in the schedule regardless of their stated airflow and heat capacities.
What makes sense from my point of view is to state the calculated ESP in the schedule, since this would provide a more defined criteria for equipment selection by the contractor who will end up executing the project (i.e. I need an FCU that can provide X CFM at Y ESP).
#2. For small FCUs, there is no Fan Curve provided and what I have is FCU airflows at ESP increments of 0.05 in.wg. It is very unlikely that my calculated ESP will coincide with any one of these points exactly. The only solution I can think of is plotting these points and generating the fan curve myself.
On the other hand I am thinking that I'm trying to be too detailed since this is not exactly a critical application (as stated above, it's a residence). Is it acceptable if the eventual airflow upon installation deviates from the one stated in the schedule? As in, Equipment Schedules are guidelines for the contractors and not something that is to be executed precisely.
I apologize if my post is too long. Thank you.