Fan and dumper

Status
Not open for further replies.

nbog

Chemical
Apr 12, 2000
40
I have always worked with fans/cyclones in a way that I had to close dumper when starting a fan. Now I've got small fan with variable speed motor so I am thinking that this time I would just have to increase the speed slowly as pressure drop (this time I am using bag filters instead of cyclones) profile establishes in the system. No need to worry about motor amperage going through the roof. Is this correct?

Thanks,
Nick
 
Replies continue below

Recommended for you

That is right, but the damper issue is not same for all types of fans.

Axial fans should always be started with full open discharge as the power consumption at dead head is more for axial fans.

Radial fans behave in a manner as you observed and their power consumption is lower at shut off condition. You can specifiy ramp up time for the fan speed, depending upon your requirement, and this works well without any problem.

 
Thanks quark. Yes, both are radial fans.
 