brad37
Mechanical
- May 17, 2010
- 1
I have an issue regarding fan selection for an AHU application with relatively low volume and high external static (in SI units) 500l/s @ 320Pa (total fan pressure approx 450Pa). In order to get a workable fan speed(no higher than 2000rpm), the available fan sizes (backward curved centrif) have a low discharge velocity (in the order of 5m/s). Typical selections by choice would be 8-9m/s. What is the effect on the fan performance in the system with a low discharge velocity and hence low velocity pressure?? I have looked through the ashrae handbook and cant find any reference to issues with lower discharge velocities.
Thanks in advance
Thanks in advance