Fan Inlet Connection Loss Coefficient

Status
Not open for further replies.

IanVG

Mechanical
Jan 21, 2022
76
Hello all. I'm looking into the pressure drop associated with a lab exhaust system that was just installed (see picture below). Specifically, I'm stuck now on the pressure drop that occurs the last 4-gore elbow to the exhaust fan inlet. The exhaust fan is a centrifugal blower. Having perused this online forum and the available ASHRAE books (I do not have the duct fitting database unfortunately), I'm not sure what method to use to find the total pressure drop from the elbow to the inlet of the fan. There are two approaches:

[ol 1]
[li] Use one of the ED7-* Fan Inlet loss coefficient tables provided by ASHRAE (I have ED7-1 or ED7-2). ED7-2 is the most applicable. For this approach (I think) I would not include the flexible duct connection/duct expansion joint or the round-to-round transition, as it appears to be covered by the ED7-2 pressure drop.[/li]

[li] Or, I can calculate the pressure drop piece by piece. I would use an approximation based on the roughness of the duct expansion joint (neoprene) and table SD4-1 for the loss coefficient for the round-to-round transition. [/li]
[/ol]

Both of these approaches seem unsatisfactory because, Approach 1 does not account for the duct expansion joint and the round-to-round transition while Approach 2 does not account for the Fan System Effect Coefficient. I believe there will be a Fan System Effect Coefficient because the 5*d (d=diameter of duct=12"Ø in this case) length requirement (by requirement I mean rule of thumb in the office, because I have also seen that 3*d may be sufficient in other cases-this may depend on the type of elbow) for the straight duct to develop laminar flow after the elbow was not met.

Does anyone have any guidance or advice on this issue?

Fan_Inlet_Connection_tp93yd.jpg
 
Replies continue below

Recommended for you

A sketch of the set up with identification of all the components mentioned in your OP would be a better approach instead of a picture. Also a performance curve of the fan which you can get from the manufacturer is needed to determine the pressure drop of the system.
 
Alright - not in the office right now. But when I get back, I'll provide a sketch (with their associated pressure drop ID or manual inputs) and a excel sheet that I put together. Thanks for the advice.
 