Been reading a few threads about using fan laws, but I think they're incorrect and I need some reassurance.
If you have a fan and change its speed while keeping the same pressure change over the fan, then you can use the 1st fan law. But if you have it connected to a ducting system, you have to follow the system curve with the new fan curve from the different speed. For example, if I cut the RPM in half, my new CFM will be more than half the first CFM because the back pressure is also reduced (lower air flow=> lower friction loss).
Sound right? Do I incorporate the new expected system pressure (second fan law) as well?
Been reading a few threads about using fan laws, but I think they're incorrect and I need some reassurance.
If you have a fan and change its speed while keeping the same pressure change over the fan, then you can use the 1st fan law. But if you have it connected to a ducting system, you have to follow the system curve with the new fan curve from the different speed. For example, if I cut the RPM in half, my new CFM will be more than half the first CFM because the back pressure is also reduced (lower air flow=> lower friction loss).