QualityTime
Civil/Environmental
- Apr 14, 2010
- 458
Hi All,
I have a NYB vane axial fan with a 25 HP motor on a pulley and it draws about 18 HP running load. On startup the fan screeches very very loudly. A pulley alignment check was made by the fan contractor and supposedly everything is okay. The belt is tight. The belt supposedly shows powdery wear on all sides of the belt. The fan aligment contractor advises the motor has too much torque capability and the belt is slipping on startup. He advises to put on a vfd to get a softer start. Something that he is saying is not right. Any comments? Thanks
I have a NYB vane axial fan with a 25 HP motor on a pulley and it draws about 18 HP running load. On startup the fan screeches very very loudly. A pulley alignment check was made by the fan contractor and supposedly everything is okay. The belt is tight. The belt supposedly shows powdery wear on all sides of the belt. The fan aligment contractor advises the motor has too much torque capability and the belt is slipping on startup. He advises to put on a vfd to get a softer start. Something that he is saying is not right. Any comments? Thanks