fastline12
Aerospace
- Jan 27, 2011
- 306
This is a full Fanuc VFD/motor unit for a spindle. The spindle is high mass and accelerates/decelerates constantly. On slower RPM accelerations, I can hear pulses of acceleration from the spindle rather than smooth. Once the motor is running around 2000rpm, it runs smooth through RPM changes.
While running, I tested the incoming voltage to the VFD to detect voltage drop. It fluctuates a bit but mostly stable. Nominal voltage should be 220V and my voltages are running 234, 231, 236. Those numbers will drop about 5-7V during acceleration.
However, I decided to test the frequency on the input side of the VFD and seeing frequency all over the map. spikes to 70hz and lows down to 20hz.
The motor is rated for 28A cont at 200V (Jap). I am running a double motor rotary phase converter that I did balance very well with caps. You can hear and see them shake during this hard accel issue. The sizing for the converter system is 20HP. This is all fed with a 25KVA utility transformer that is shared so I feel certain the transformer is being over driven but that usually causes voltage drop, not frequency issues?
During these slow accelerations, you can almost hear those IGBT gates going to 100% duty trying to get the spindle up. I am not sure if the slower speed of the motor and inherent very low VFD output frequency is amplifying the issue?
Any thoughts, ideas, or system checks we can do would help. I am not sure that my frequency checks are reliable as the harmonics on the line could do that. Might be time to drag the scope out.
While running, I tested the incoming voltage to the VFD to detect voltage drop. It fluctuates a bit but mostly stable. Nominal voltage should be 220V and my voltages are running 234, 231, 236. Those numbers will drop about 5-7V during acceleration.
However, I decided to test the frequency on the input side of the VFD and seeing frequency all over the map. spikes to 70hz and lows down to 20hz.
The motor is rated for 28A cont at 200V (Jap). I am running a double motor rotary phase converter that I did balance very well with caps. You can hear and see them shake during this hard accel issue. The sizing for the converter system is 20HP. This is all fed with a 25KVA utility transformer that is shared so I feel certain the transformer is being over driven but that usually causes voltage drop, not frequency issues?
During these slow accelerations, you can almost hear those IGBT gates going to 100% duty trying to get the spindle up. I am not sure if the slower speed of the motor and inherent very low VFD output frequency is amplifying the issue?
Any thoughts, ideas, or system checks we can do would help. I am not sure that my frequency checks are reliable as the harmonics on the line could do that. Might be time to drag the scope out.