Scenario:
Say there is a small power station being fed by 10 diesel gen-sets on a common bus running at 11kV and being stepped up off the bus feeder to 22kV for distribution and somewhere on the network 22kV there is a fault to earth.
The fault current will be accompanied by a voltage dip at the gen-sets, correct?
Question:
The fault current and the impedance of the path to earth will appear as a step load to the gen-sets and cause them to get bogged down and stall, however to calculate if that fault will be cleared in time without stalling them i need to look at the protection curves on that feeder. If after doing that, i can ascertain that the fault should be cleared in 0.6s by the CB, i now need to see what happens to that gen-set within 0.6s of the fault conditions. How do i calculate what that step load will be? Do I need to know the voltage dip? How do I work that out?
It seems to me that the calculations that I did assuming the system to be at 22kV to determine the fault current may be wrong given that the voltage will dip below that. I seem to have used a static-type calculation that doesn't take the transient nature of the voltage into account.
Any and all help is appreciated !
Cheers,
Matt.
Say there is a small power station being fed by 10 diesel gen-sets on a common bus running at 11kV and being stepped up off the bus feeder to 22kV for distribution and somewhere on the network 22kV there is a fault to earth.
The fault current will be accompanied by a voltage dip at the gen-sets, correct?
Question:
The fault current and the impedance of the path to earth will appear as a step load to the gen-sets and cause them to get bogged down and stall, however to calculate if that fault will be cleared in time without stalling them i need to look at the protection curves on that feeder. If after doing that, i can ascertain that the fault should be cleared in 0.6s by the CB, i now need to see what happens to that gen-set within 0.6s of the fault conditions. How do i calculate what that step load will be? Do I need to know the voltage dip? How do I work that out?
It seems to me that the calculations that I did assuming the system to be at 22kV to determine the fault current may be wrong given that the voltage will dip below that. I seem to have used a static-type calculation that doesn't take the transient nature of the voltage into account.
Any and all help is appreciated !
Cheers,
Matt.