Dear Folks,
For Isolated generation system-LV (Without grid), our contractor submitted the following fault calculation.
0.5 cycle fault current:145kA Assymetrical Peak
1.5 to 4 cycle fault current-105kA Symmetrical rms
30 cycle fault current- 70 kA symmetrical rms (60 Hz system, )
Contractor selected circuit breaker with breaking current 75kA and short-circuit with-stand current :75kA, 1-sec (Scneider breaker), Making current-160kA. And contractor explanation is --The complete system is designed to short circuit with-stand current i.e. 75kA for 1-sec. Contractor is setting the protective relay to open the breaker with time delay 0.5 sec (fault current will decay to less than 75kA with this time delay)instead of designing 1.4 to 4 cycle fault current i.e.105kA
Is it allowable to keep the system without tripping for 0.5 sec, for the above fault currents however it is designed for 1-sec? What is effect of arc flash for 0.5sec?
And also contractor not considered motor contribution 500kW - motors as all motors are operated with Variable frequency drives (Altivar 61). It is a 6-pulse VFD. If VFD is there, is there no possibility of contributing fault current by motor?
Pl. share ur knowledge in this regard,
Advanced thanks a lot..
For Isolated generation system-LV (Without grid), our contractor submitted the following fault calculation.
0.5 cycle fault current:145kA Assymetrical Peak
1.5 to 4 cycle fault current-105kA Symmetrical rms
30 cycle fault current- 70 kA symmetrical rms (60 Hz system, )
Contractor selected circuit breaker with breaking current 75kA and short-circuit with-stand current :75kA, 1-sec (Scneider breaker), Making current-160kA. And contractor explanation is --The complete system is designed to short circuit with-stand current i.e. 75kA for 1-sec. Contractor is setting the protective relay to open the breaker with time delay 0.5 sec (fault current will decay to less than 75kA with this time delay)instead of designing 1.4 to 4 cycle fault current i.e.105kA
Is it allowable to keep the system without tripping for 0.5 sec, for the above fault currents however it is designed for 1-sec? What is effect of arc flash for 0.5sec?
And also contractor not considered motor contribution 500kW - motors as all motors are operated with Variable frequency drives (Altivar 61). It is a 6-pulse VFD. If VFD is there, is there no possibility of contributing fault current by motor?
Pl. share ur knowledge in this regard,
Advanced thanks a lot..