davva
Marine/Ocean
- Sep 27, 2004
- 99
If you have 4 generators in parallel each capable of supplying 10kA fault current, could you able the argument:-
With all generators running and for a fault on the cables of one generator, would the maximum fault current seen by that cable be 3 x 10kA, rather than 4 x 10kA? (obviously approx. 4 x 10kA flows into the fault with 3 parts being supplied by 3 sets and 1 part being supplied by the faulted generator). This argument is being put forward to me as part of a protection study which includes I2t protection of the cables.
All sounds good in terms of Kirchoffs but I've always worked on the basis that the switchboards and cables would all be rated on maximum fault level.
With all generators running and for a fault on the cables of one generator, would the maximum fault current seen by that cable be 3 x 10kA, rather than 4 x 10kA? (obviously approx. 4 x 10kA flows into the fault with 3 parts being supplied by 3 sets and 1 part being supplied by the faulted generator). This argument is being put forward to me as part of a protection study which includes I2t protection of the cables.
All sounds good in terms of Kirchoffs but I've always worked on the basis that the switchboards and cables would all be rated on maximum fault level.