Is there anyway to calculate by how much fault current increases with a Yd11 vs a Dyn11 132-33kv transformer on the primary side duding a 132kv fault?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Kiribanda said:Mbrooke,
I think you are looking for the increase in ground fault current happens when the transformer is YNd11 (solidly grounded WYE on 132kV Utility side). During a ground fault on 132kV side, in addition to the ground fault contribution from the Utility side, there will be a a zero seq current contribution from the primary of the transformer too. Therefore the actual ground fault current at the fault location is higher. But this will not happen if the transformer is Dyn11 because the DELTA winding is not a zero seq source. One thing important here is that if the transformer is YNd11 then during such a ground fault on 138kV side the Utility current contribution becomes little lower. (If you model and calculate you will find this) Depending on the ground fault pick-up setting this lower fault current may not trip the Utility upstream bkr. Therefore, Utility has to adjust 50/51G accordingly. Is this the answer you are looking for or otherwise?