Recently we had an incident involving a falling branch on an LV power line which energised a colour-bond fence.
Our (protection) fuses are generally set to operate above specific load currents in order to facilitate overload tripping. Faults involving vegetation are often high resistive earth faults that are accompanied by arcing. In this case the fault current was considerably lower than the normal system load current. As a result, the protection system was unable to pick up low residual earth fault current. In this instance the fallen power lines came to ground and remained live constituting a major hazard for the general public.
I am just a tad confused as to why the current level was considerably lower than the normal system load current if it was a short circuit fault and the resistance to ground is reduced due to the conductivity of the colourbond fence (even more if the fence is earthed).
Our (protection) fuses are generally set to operate above specific load currents in order to facilitate overload tripping. Faults involving vegetation are often high resistive earth faults that are accompanied by arcing. In this case the fault current was considerably lower than the normal system load current. As a result, the protection system was unable to pick up low residual earth fault current. In this instance the fallen power lines came to ground and remained live constituting a major hazard for the general public.
I am just a tad confused as to why the current level was considerably lower than the normal system load current if it was a short circuit fault and the resistance to ground is reduced due to the conductivity of the colourbond fence (even more if the fence is earthed).