Modula2
Electrical
- Aug 3, 2002
- 81
Has there been any concensus on which currents to use as bolted fault current on MV, Hi-R grd systems. I ask because arc flash standards caution against overly conservative fault calcs. However, fault calculation standards are just that. I have a max level from Ansi C37 momentary 0-1 cycle. For 1.5-4 cycles, there is the C37 interrrupting level, where motors have reduced contribution compared to mom. All motors OFF is a minimum level. L-L for all these is also a possible occurrence. That leaves max from C37 mom., and min with motors OFF, L-L fault. I did not see asymmetrical currents involved in arc flash calc standards (unless I missed it). Thanks