What is the cause of an arcing fault inside of a generator terminal box? Here is some background info:
Generator system consists of (2) 1500 kW, 13.2 kV diesel generators operating in parallel. The neutral of each generator is grounded through a neutral grounding resistor.
The units were operating for about three hours when one unit tripped. The unit was started again and immediately tripped. The next day, the unit was started again and the operator noticed that there was no current in phase c. He shut the unit down and inspected the terminal box. Phase C connector had burned of the bus bar. Apparently there was an arcing fault between phases which jumped between all three phases and the neutral bus bar. Information downloaded from the protective relay indicated that no ground current flowed through the resistor (a loose connection was found at the resistor). The only damage to the system was to the bolts that connected the lugs to the bus bars - the bolts on each phase and neutral was melted, with material dripping of the ends. There are several marks on the terminal box door apparently from arcing to ground.
After repairing the lugs, the generator was tested and was found to be in good condition. The system is now running.
What could have caused this to happen?
Generator system consists of (2) 1500 kW, 13.2 kV diesel generators operating in parallel. The neutral of each generator is grounded through a neutral grounding resistor.
The units were operating for about three hours when one unit tripped. The unit was started again and immediately tripped. The next day, the unit was started again and the operator noticed that there was no current in phase c. He shut the unit down and inspected the terminal box. Phase C connector had burned of the bus bar. Apparently there was an arcing fault between phases which jumped between all three phases and the neutral bus bar. Information downloaded from the protective relay indicated that no ground current flowed through the resistor (a loose connection was found at the resistor). The only damage to the system was to the bolts that connected the lugs to the bus bars - the bolts on each phase and neutral was melted, with material dripping of the ends. There are several marks on the terminal box door apparently from arcing to ground.
After repairing the lugs, the generator was tested and was found to be in good condition. The system is now running.
What could have caused this to happen?