We have a gen set consisting of a 5oo MVA generator and a 0.415/11 kV Traffo. The generator has Xd'= 15.9 %, Xd''= 11.1 %. The Traffo has z = 4.58%. I have calculated the fault level but its too high.

May be there is something I have forgotten and please remind me which of the generator reactances is appropriate

Thank you guys in advance.
 
Replies continue below

Recommended for you

A 500MVA set directly connected to a 0.415/11kV transformer? Check your post and confirm the data you posted - something does not sound quite right.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Connection to the tarffo is via a circuit breaker
 
Hi Punglu.
Maybe it's 500KVA!!! Please see again Scotty's post.
Regards.
Slava
 
Oops sorrry for that, its 500kVA!!!
 
For calculate fault current, you should use Z"dv, so X"d = 11% in your case. For this size of generator, you can take typical value of X/R of induction motor, approximately 15-20 for 500kVA
 