Bung
Electrical
- Feb 10, 2002
- 428
I'm interested in hearing about how people out there deal with the problem of controllong fault levels in 11kV distribution substations. Our nominal maximum (design) fault level is 13kA (250MVA). Recent plans to augment some substations by adding another transformer means that the fault level will go above this (and beyond the CB capacity) unless we take action to limit it. I'm sure our frineds in the petro-chem and other heavy industries would know all about this problem!
Methods I have come across include:
1] reactors in bus-sections between transformers
2] high Z trnasformers ( I can think of lots of downsides to this one, and few upsides).
3] electronically controlled explosive powered "fault current limiters
4] saturable reactors, traditional magnetic amps or superconducting magnetic amps.
5] running split bus and putting up with short duration interruptions for transformer faults (I like this one -KISS)
Any thoughts out there?
Bung
Methods I have come across include:
1] reactors in bus-sections between transformers
2] high Z trnasformers ( I can think of lots of downsides to this one, and few upsides).
3] electronically controlled explosive powered "fault current limiters
4] saturable reactors, traditional magnetic amps or superconducting magnetic amps.
5] running split bus and putting up with short duration interruptions for transformer faults (I like this one -KISS)
Any thoughts out there?
Bung