When you size a cable for fault rating do you use the "asymmetrical" or "symmetrical rms" fault current at the point of concern in the network.
I realise it is the I^2xt heating effect that is used in the standard adiabatic formula for sizing the cable. The formula is relevant for faults between 0.2secs and 5secs, so is it taken that the DC offet current has decayed to zero by this time (0.2secs). What happens below 0.2secs? I had convinced myself I knew the answer but now I'm not so sure!!
I would also be interested in hearing from people who have any experience in "undersizing" cables, i.e. selecting a cable which would exceed the "recommended" final conductor temperature for a given fault current and disconnection time, e.g. taking a conductor (rated for 250degC) to 300degC. Would it catch fire? Would the insulation become brittle? The intention would be to replace the cable after the short circuit had occured, i.e. it would not see repeated short circuits. (The cable would be suitably braced for electromechanical forces). I guess what I'm also asking is when they say final conductor temperature do they mean final or is there any headroom?
I realise it is the I^2xt heating effect that is used in the standard adiabatic formula for sizing the cable. The formula is relevant for faults between 0.2secs and 5secs, so is it taken that the DC offet current has decayed to zero by this time (0.2secs). What happens below 0.2secs? I had convinced myself I knew the answer but now I'm not so sure!!
I would also be interested in hearing from people who have any experience in "undersizing" cables, i.e. selecting a cable which would exceed the "recommended" final conductor temperature for a given fault current and disconnection time, e.g. taking a conductor (rated for 250degC) to 300degC. Would it catch fire? Would the insulation become brittle? The intention would be to replace the cable after the short circuit had occured, i.e. it would not see repeated short circuits. (The cable would be suitably braced for electromechanical forces). I guess what I'm also asking is when they say final conductor temperature do they mean final or is there any headroom?