Hello,
I have a 13800-1050Y/606 transformer that is resistance grounded on the secondary with a 17.4K NGR. All the necessary GF relays are in-place. However, we would like to install a ground fault test unit on one of the phases to ground. It basically consists of a fused (2A fuse) contact from a test contactor in series with a 15K,100W variable resistor.
My question is:
Is a 600V rating sufficient for the fuse, contactor arrangment? Or is the line voltage of 1050V required?
I know the phase voltage is all the tester will normally see, however during a fault on another phase will the tester phase not see a larger value than Vphase? If so what would be the value?
I have a 13800-1050Y/606 transformer that is resistance grounded on the secondary with a 17.4K NGR. All the necessary GF relays are in-place. However, we would like to install a ground fault test unit on one of the phases to ground. It basically consists of a fused (2A fuse) contact from a test contactor in series with a 15K,100W variable resistor.