cuky2000
Electrical
- Aug 18, 2001
- 2,133
Hello all,
We do have a 12 kV delta ungrounded source transformer feeding a station service transformer Wye/grounded via an underground 15kV cable rated for with 133% Insulation level . The selection of the cable insulation became a divided opinion in the event of ground fault as follow:
* Opinion 1: The fault will create essentially a corner delta generating only small current that may not be sufficient to trip the fuses. On a second ground fault, the associated fuses will blow up. This group recommend cable rated for 15kV and 173% insulation or 25 kV 100% Insulation to maintain the raised voltage for long term.
* Opinion 2: Other engineers believe that the current will be high enough to blow the 3-12 kV fuses and protect the feeder and transformer clearing the fault quick. Therefore, this group consider that the 15 kV cable with 133% insulation level is adequate for this application since will trip the fault in less than 1 minute.
All group concur if the load is a delta ungrounded transformer, the fuses will not blow up because the mall current.
please let us know your thoughts on this matter.
We do have a 12 kV delta ungrounded source transformer feeding a station service transformer Wye/grounded via an underground 15kV cable rated for with 133% Insulation level . The selection of the cable insulation became a divided opinion in the event of ground fault as follow:
* Opinion 1: The fault will create essentially a corner delta generating only small current that may not be sufficient to trip the fuses. On a second ground fault, the associated fuses will blow up. This group recommend cable rated for 15kV and 173% insulation or 25 kV 100% Insulation to maintain the raised voltage for long term.
* Opinion 2: Other engineers believe that the current will be high enough to blow the 3-12 kV fuses and protect the feeder and transformer clearing the fault quick. Therefore, this group consider that the 15 kV cable with 133% insulation level is adequate for this application since will trip the fault in less than 1 minute.
All group concur if the load is a delta ungrounded transformer, the fuses will not blow up because the mall current.
please let us know your thoughts on this matter.