I have a small 13,000 sqft rectangle non-combustible single story building. The single light hazard 2" wet system riser is in the back (south side) of the building. I have a 2" primary main running east & west at the back of the building fed from the 2" riser and a floating 2" secondary main running east & west at the front of the building. The branchlines (running north & south) between them are all 1 1/4" sch 40 with 1 1/4" riser nipples ( no out riggers). The branchlines are 75' long. The grid system is hydraulically calculated with a large safety factor.
The FDC is located on the front of the building. It is a single 2 1/2" connection fed with 2" pipe from the secondary 2" main.
To be clear - all mains, wet riser, and FDC feed piping are 2" sch 40. All gridded branchlines are 1 1/4" sch 40.
NFPA 13 (2019 Handbook) 16.12.5.1 states that a single wet system can have the FDC attached to any point of a feed main or cross main in the system provided you use the required pipe sizes. It also states the FDC connection not be attached to branchlines.
It does not call out any exceptions for a grid system.
The problem I'm having is the Fire Marshal says I have to tie the primary & secondary mains together with 2" pipe because the 1 1/4" branchlins are not big enough to get water to the primary main from the FDC. Or I could have made on of the branchlines 2". He saying that I'm interpenetrating the codes incorrectly and the codes would not allow a remote FDC be attached to a secondary main of a grid system.
Who is right?? How do you interpret these codes?
Thank you for the help.
JC
The FDC is located on the front of the building. It is a single 2 1/2" connection fed with 2" pipe from the secondary 2" main.
To be clear - all mains, wet riser, and FDC feed piping are 2" sch 40. All gridded branchlines are 1 1/4" sch 40.
NFPA 13 (2019 Handbook) 16.12.5.1 states that a single wet system can have the FDC attached to any point of a feed main or cross main in the system provided you use the required pipe sizes. It also states the FDC connection not be attached to branchlines.
It does not call out any exceptions for a grid system.
The problem I'm having is the Fire Marshal says I have to tie the primary & secondary mains together with 2" pipe because the 1 1/4" branchlins are not big enough to get water to the primary main from the FDC. Or I could have made on of the branchlines 2". He saying that I'm interpenetrating the codes incorrectly and the codes would not allow a remote FDC be attached to a secondary main of a grid system.
Who is right?? How do you interpret these codes?
Thank you for the help.
JC