Haldorson
Mechanical
- Mar 27, 2011
- 92
Hello all,
Consider a highrise equipped with a booster pump and two PRV's, one serving the dry zones in the parkade and one serving the Class I standpipe system. The PRV supplying the dry zones is set to 165 psi, the PRV supplying the Class I standpipe is set to 240 psi.
From what I understand we have two options with respect to the tie-in locations of the FDC's:
(1) Tie-in both required siamese FDC's downstream of the booster pump and upstream of both PRV's, OR
(2) Have a total of four siamese FDC's. A low and high pressure FDC for each remote FDC staging location. All FDC's are tied in downstream of both the booster pump AND the appropriate PRV's (ie, max pressure FDC's of 165 psi downstream of PRV serving the dry zones and max pressure 240 psi FDC's downstream of PRV serving Class I standpipe).
Thoughts?
Also, if the above is true, is the only advantage of using a high and low pressure FDC to reduce the run of 4" back to the valve station to tie-in upstream of the PRV's?
Thanks.