Feeder loading 1

Status
Not open for further replies.

thinker

Electrical
Aug 2, 2001
247
Dear colleagues,
We need to connect a 800 kVA transformer (480/480)to user grid. The available single busplug is sized for approximately a half of transformer FLA. Is it possible and/or legal to use 2 busplugs to feed a transformer via 2 parallel branches (assuming their equal length)?
 
Replies continue below

Recommended for you

My question would be are the bus plugs physically close together. If so you could bring the conductors into a fused disconnect switch and on to the transformer. The fuse would be size for the transformer per 450.3(B). The scondary would be protected per 240.21C.
 
I would like to clarify my question: I am talking about 2 fusible busplug tap-offs which in sum provide needed ampacity, can I feed a single load (transformer) from 2 parralel and protected (?)branches?
 
I don't see a section in the code (NEC) that prohibits it, but it may not be the best practice.

Mike
 
Not according to the NEC.

Article 240: "Fuses and circuit breakers shall be permitted to be connected in parallel where they are factory assembled in parallel and listed as a unit. Individual fuses, circuit breakers or combinations thereof shall not otherwise be connected in parallel."
 
Alehman,
Thanks for very good reference.
 