I wanted to get others opinion on protection functions for a 4.16kV Switchgear feeder breaker that feeds a provision for an external roll-up generator.
Usually in a situation with permanent generator the feeder breaker may have all gen protection functions (87G, 32, etc..) however in this application the portable/temporary generator has an internal breaker with its own protection and control. With that being the case I'm thinking that the feeder breaker in the switchgear simply becomes a feeder breaker with 50/51 functions only that simply coordinate with any 50/51 or 51V functions internal to the generator?
There is also the possibility that on rare occasions the generator will operate in parallel with an incoming utility source to the switchgear. The feeder breaker would close to provide the utility voltage source to the generator and the generator would then have its own internal sync check to sync to utility and close its breaker. Thus I am thinking that no sync check (25) is required on feeder breaker?
If there is a case however where the generator is operating in an islanded condition and the utility source comes back online there will need to be a sync check function at the main breaker, in order to transfer back to utility to keep gen online.
Based on this do others agree that only 50/51 is needed at gen feeder, and main breaker should have 25 sync function?
Usually in a situation with permanent generator the feeder breaker may have all gen protection functions (87G, 32, etc..) however in this application the portable/temporary generator has an internal breaker with its own protection and control. With that being the case I'm thinking that the feeder breaker in the switchgear simply becomes a feeder breaker with 50/51 functions only that simply coordinate with any 50/51 or 51V functions internal to the generator?
There is also the possibility that on rare occasions the generator will operate in parallel with an incoming utility source to the switchgear. The feeder breaker would close to provide the utility voltage source to the generator and the generator would then have its own internal sync check to sync to utility and close its breaker. Thus I am thinking that no sync check (25) is required on feeder breaker?
If there is a case however where the generator is operating in an islanded condition and the utility source comes back online there will need to be a sync check function at the main breaker, in order to transfer back to utility to keep gen online.
Based on this do others agree that only 50/51 is needed at gen feeder, and main breaker should have 25 sync function?