CanuckEngineer
Electrical
- Feb 9, 2009
- 45
Hello all.
I have read many postings/threads on this site over the last few years.
I have decided to join, not only to further my own personal knowledge but to be able to help others, which I believe is more important, because you help others your understanding grows that much more.
I work as an electrical design engineer up here in Toronto, Canada. I work for a dealer that sells generator and switchgear equipment, for the Standby and Prime POwer industries.
Lately I have been getting into more and more complex projects, involving multi paralleled gensets to Utility, peak shaving, relay protection etc.
Slowly learning all the ins and outs of this industry.
I have the following question.
We have a multiple generator set appliation. Six to be in fact which are to be paralleled and tied to a common bus. The generators are somewhat large, in termns of reciprocating type, they are rated at 2250eKw at 13.8kV voltage.
Now, we have Sr489 protection relays for each genset on the aux. switchgear.
The consultant has come back and asked what is protecting the feeder or cable connection between the generator and the switchgear.
They are asking if their is an internal fault, i.e. upstream of the protection relay and its associated CT's. What will trip the gen. breaker and what would shut down the genset.
I was reading up on this, and I wanted to ask you guys on whether Differential GEnerator protection would apply here, 87G?
We do have 6 lead genset and we do have 3 CT's mounted on the generator side for this differential protection, with the matching set on the switchgear, both sets feeding into the SR489.
Will differential protection on the SR489, i.e. 87G, be sufficient in short circuit or over current situations right on the generator?
What could be some of my other options here.
Much thanks guys,
CanuckEngineer.
I have read many postings/threads on this site over the last few years.
I have decided to join, not only to further my own personal knowledge but to be able to help others, which I believe is more important, because you help others your understanding grows that much more.
I work as an electrical design engineer up here in Toronto, Canada. I work for a dealer that sells generator and switchgear equipment, for the Standby and Prime POwer industries.
Lately I have been getting into more and more complex projects, involving multi paralleled gensets to Utility, peak shaving, relay protection etc.
Slowly learning all the ins and outs of this industry.
I have the following question.
We have a multiple generator set appliation. Six to be in fact which are to be paralleled and tied to a common bus. The generators are somewhat large, in termns of reciprocating type, they are rated at 2250eKw at 13.8kV voltage.
Now, we have Sr489 protection relays for each genset on the aux. switchgear.
The consultant has come back and asked what is protecting the feeder or cable connection between the generator and the switchgear.
They are asking if their is an internal fault, i.e. upstream of the protection relay and its associated CT's. What will trip the gen. breaker and what would shut down the genset.
I was reading up on this, and I wanted to ask you guys on whether Differential GEnerator protection would apply here, 87G?
We do have 6 lead genset and we do have 3 CT's mounted on the generator side for this differential protection, with the matching set on the switchgear, both sets feeding into the SR489.
Will differential protection on the SR489, i.e. 87G, be sufficient in short circuit or over current situations right on the generator?
What could be some of my other options here.
Much thanks guys,
CanuckEngineer.