For the typical industrial deaerator, a steam pressure reducing valve controls steam for heating incoming water at the deaerator to saturation temperature. Normally, the deaerator operates at 5 psig; exiting boiler feedwater is 227°F.
When condensate return water is 227°F or above, it is returned directly to the deaerator storage tank. Any condensate
below 227°F must be deaerated. Incoming makeup water is typically in the range of 55-70 °F.
Released dissolved oxygen and carbon dioxide gases along with a negligible steam loss of approximately one tenth of 1% are vented out of the roof of the deaerator.