Is there a rule of thumb on how much temperature rise you would expect in a deaerator for boiler feedwater to and from the deaerator?

I'm assuming some of the heat from deaeration gets transferred to the incoming feedwater.

Thanks in advance.
 
Replies continue below

Recommended for you

For the typical industrial deaerator, a steam pressure reducing valve controls steam for heating incoming water at the deaerator to saturation temperature. Normally, the deaerator operates at 5 psig; exiting boiler feedwater is 227°F.

When condensate return water is 227°F or above, it is returned directly to the deaerator storage tank. Any condensate
below 227°F must be deaerated. Incoming makeup water is typically in the range of 55-70 °F.

Released dissolved oxygen and carbon dioxide gases along with a negligible steam loss of approximately one tenth of 1% are vented out of the roof of the deaerator.
 
Normally Deaerator water is at saturation temperature corresponding to the operating pressure.
 