FF in a Floodplain

Status
Not open for further replies.

GoldDredger

Civil/Environmental
Jan 16, 2008
172
For construction of a building within a 100 year flood plain, what is the height above WSE in your area?

I was discussing with a collegue here in Texas who indicated finished floor needs to be 2-feet above the 100 year WSE. I seem to recall in Utah and California it was 1.5-feet.

(Intended as a generic question and assuming the building or developement itself does not alter the elevation of the flood plain)

Anyone have a strong opinion of this either way?
 
Replies continue below

Recommended for you

The finished floor elevation should be elevated above the Advisory Base Flood Elevation (BFE).
 
As Miketheengineer says, check with the local Authority. It is not a matter of opinion, but a matter of law or regulation. FEMA prescribes minimum standards but local agencies; Cities, Counties, Flood Control Districts, etc. may require stricter standards. FEMA's standard is 1 foot above the Base Flood Elevation (BFE) but often that elevation is unknown. In such a case, one County I know requires 2 feet above the highest adjacent ground. Others require different separation but any such agency may require anything they feel comfortable with which is stricter than FEMA's.
 