Wanted to get the forum's thoughts on a recent construction issue I've had with a reinforced concrete foundation for a large pump skid. The foundation is roughly a large rectangular block consisting of ~25 cu yards of reinforced concrete. Our project manager insisted we specify fiber mesh to be added in the concrete mix design for this foundation. The idea being the fiber mesh would help in controlling cracks/shrinkage on this foundation. A number of engineers working under the PM questioned the need for fiber mesh, especially in a large section block foundation like this. My understanding is fiber mesh is typically only used in thin section concrete mix designs (slabs, panels, etc). The client & contractor also had some push back on adding fiber mesh for this foundation since they'd never encountered this before. In the end, they went ahead with it.
The foundation was poured using a pump truck on a 50 deg F day. Based on site photos, the contractor appeared to cover the top the foundation with an insulating blanket after the pour. I have not been able to determine if the fiber mesh was added at the plant or on site yet.
About 10 days after the pour, the contractor returned to begin chipping the top surface of the foundation down ~1" deep to prepare for grouting the pump skid baseplate to it. Upon chipping, the contractor encountered extremely weak & crumbling concrete on the top surface. Concrete was chipping off in large chunks & the large chunks could be broken apart by hand. Looking at site photos, it looks to me that there is way too much fiber mesh in the top few inches of this foundation block. Also, the color of the chipped concrete did not look uniform like it does when most concrete cures properly, but I'm not an expert on judging this.
There is no indication that excess water was added to the mix on site. The w/c ratio appears to be fine based on the tickets. The lab test breaks show no signs of bad concrete either. The design strength was 4500 psi. The three (3) 7-day breaks we had came back at ~4000 psi, which was a little higher than expected.
Any ideas what went wrong here?
Obviously there are a lot of things can wrong in something like this, but my initial thought is with the contractor being unfamiliar with the fiber mesh mixing & placement. Could there have been issues with how the fiber mesh was added, mixed, & ultimately placed & finished? One thought was the lighter fiber mesh material may have floated up toward the top few inches of this foundation block and prevented the concrete in this area from properly binding/chemically reacting like it should have?
Tolerance is the virtue of the man without convictions -GK Chesterton
The foundation was poured using a pump truck on a 50 deg F day. Based on site photos, the contractor appeared to cover the top the foundation with an insulating blanket after the pour. I have not been able to determine if the fiber mesh was added at the plant or on site yet.
About 10 days after the pour, the contractor returned to begin chipping the top surface of the foundation down ~1" deep to prepare for grouting the pump skid baseplate to it. Upon chipping, the contractor encountered extremely weak & crumbling concrete on the top surface. Concrete was chipping off in large chunks & the large chunks could be broken apart by hand. Looking at site photos, it looks to me that there is way too much fiber mesh in the top few inches of this foundation block. Also, the color of the chipped concrete did not look uniform like it does when most concrete cures properly, but I'm not an expert on judging this.
There is no indication that excess water was added to the mix on site. The w/c ratio appears to be fine based on the tickets. The lab test breaks show no signs of bad concrete either. The design strength was 4500 psi. The three (3) 7-day breaks we had came back at ~4000 psi, which was a little higher than expected.
Any ideas what went wrong here?
Obviously there are a lot of things can wrong in something like this, but my initial thought is with the contractor being unfamiliar with the fiber mesh mixing & placement. Could there have been issues with how the fiber mesh was added, mixed, & ultimately placed & finished? One thought was the lighter fiber mesh material may have floated up toward the top few inches of this foundation block and prevented the concrete in this area from properly binding/chemically reacting like it should have?
Tolerance is the virtue of the man without convictions -GK Chesterton