AZElectrical
Electrical
- Mar 18, 2015
- 5
I have a project going on to replace the static excitation systems on four small pump/generators. The current scheme for tripping the DC field breaker has a few different modes:
[ol 1]
[li]For a split-phase differential trip, an opened excitation AC breaker, or opened PPT HV disconnect, the field breaker is opened right away, without consideration of the status of the unit circuit breaker.[/li]
[li]For all other cases, including normal shutdown and other unit lockouts (overcurrent etc.), the field breaker is opened 10 seconds after the unit slows down to 85% speed.[/li]
[/ol]
The vendor we are working with for the new system has stated that they have never seen an excitation system designed like this, and is recommending that any field breaker trips in the new system require a permissive of an open unit CB. The reasoning for this is that if the field CB opens before the unit CB, the machine will behave as an induction generator. Certainly there is merit to this line of thought, but what is causing some angst among myself and other engineers working on the project is that the system was not designed in this fashion originally (which could have been an error).
So I am posting to find out what other companies do with respect to field breaker tripping. Is it common to have any field CB trip rely on a permissive of an open unit CB prior to operation?
Thanks
[ol 1]
[li]For a split-phase differential trip, an opened excitation AC breaker, or opened PPT HV disconnect, the field breaker is opened right away, without consideration of the status of the unit circuit breaker.[/li]
[li]For all other cases, including normal shutdown and other unit lockouts (overcurrent etc.), the field breaker is opened 10 seconds after the unit slows down to 85% speed.[/li]
[/ol]
The vendor we are working with for the new system has stated that they have never seen an excitation system designed like this, and is recommending that any field breaker trips in the new system require a permissive of an open unit CB. The reasoning for this is that if the field CB opens before the unit CB, the machine will behave as an induction generator. Certainly there is merit to this line of thought, but what is causing some angst among myself and other engineers working on the project is that the system was not designed in this fashion originally (which could have been an error).
So I am posting to find out what other companies do with respect to field breaker tripping. Is it common to have any field CB trip rely on a permissive of an open unit CB prior to operation?
Thanks