Hello fellow Structural Engineers,
I have a house project in which the contractor missed building a major shear wall (1/2" plywood x 12" long x 3 stories high.)
So, one idea we have is to sheath the curved (in plan) wall that is the curved stair outside wall. It is the only full height (bsmt-roof) wall. The radius of the curve is 10 ft, and the wall is approximately, 12 ft of that length.
Our shear wall previously required 10.5 ft.
So, we previous had 1/2" plywood (both sides).
The contractor wants to use (2) layers of 1/4" plywood on each side of the curved wall, because it will easily bend to fit the curve.
I actually thought they'd be able to bend wet 1/2" plywood into that shape.
So questions:
1. Can 1/2" plywood get soaked with water, bent to curve, and not lose much strength after it dries?
2. If we glue the (2) 1/4" sheets together in the field with wood glue, will that be adequate? The (2) 1/4" sheets will also be nailed 10d@3" o.c. at the edges and 10d@12" o.c. field for shear nailing. The glue merely prevents the 1/4" sheets from buckling. And plywood is normally glued layers anyway.
I think the strength will be enough. I am concerned the glue would actually make the wall too stiff, and thus negate our R = 6.5 for earthquake analysis.
Please let me know if you have any REAL experience with this?
If you are merely guessing or speculating, please say so.
I need to know what's factual and what's not.
Thanks all! I appreciate your input!
SeattleMike!
I have a house project in which the contractor missed building a major shear wall (1/2" plywood x 12" long x 3 stories high.)
So, one idea we have is to sheath the curved (in plan) wall that is the curved stair outside wall. It is the only full height (bsmt-roof) wall. The radius of the curve is 10 ft, and the wall is approximately, 12 ft of that length.
Our shear wall previously required 10.5 ft.
So, we previous had 1/2" plywood (both sides).
The contractor wants to use (2) layers of 1/4" plywood on each side of the curved wall, because it will easily bend to fit the curve.
I actually thought they'd be able to bend wet 1/2" plywood into that shape.
So questions:
1. Can 1/2" plywood get soaked with water, bent to curve, and not lose much strength after it dries?
2. If we glue the (2) 1/4" sheets together in the field with wood glue, will that be adequate? The (2) 1/4" sheets will also be nailed 10d@3" o.c. at the edges and 10d@12" o.c. field for shear nailing. The glue merely prevents the 1/4" sheets from buckling. And plywood is normally glued layers anyway.
I think the strength will be enough. I am concerned the glue would actually make the wall too stiff, and thus negate our R = 6.5 for earthquake analysis.
Please let me know if you have any REAL experience with this?
If you are merely guessing or speculating, please say so.
I need to know what's factual and what's not.
Thanks all! I appreciate your input!
SeattleMike!