Trying to find the calculations for fill-line in tanks.
What is the height of the air space needed in a tank of fuel,oil or solivent?
I have heard its 10% of volume is a rule, but just how true is this number??
 
Replies continue below

Recommended for you

5% will do, provided the inlet flowrate is safely limited. That's a good place for a Hi Hi level alarm & auto shut-down of the fill line.

**********************
"Pumping accounts for 20% of the world’s energy used by electric motors and 25-50% of the total electrical energy usage in certain industrial facilities."-DOE statistic (Note: Make that 99% for pipeline companies)
 
API 2350 "Overfill Protction" might help you.
 