Fire Alarm Zones 3

Status
Not open for further replies.

desnov74

Electrical
Nov 14, 2007
163
I have a question regarding NFPA 72 2002 section.
In the appendix A.4.4.6.1.2 section (5)
it states that the floor area shall not exceed 22,500sq.ft.
and any length of 300ft in any direction.

Then it says if it is sprinklered, the area of the zone should be permitted to coincide with the allowable area of the the sprinkler zone. Which I read as 52,000 sq.ft.

Are there any other implicit limitations?
Does the 300ft. rule still apply?
How does this impact my number of and location of things like my DGP panels etc?

[roll1]Thanks in advance!
 
Replies continue below

Recommended for you

That provision is no longer in the 2007 edition of NFPA 72.
 
And remember, the idea is a sprinkler system reduces the risk to building occupants by increasing the time they have to get out of a building and reduces the risk to the firefighters entering a building. The fire alarm code recognizes this and allows for larger protection areas.

Don Phillips
 
I read through 72's current version as cdafd, and came up with the same answer as stookeyfpe. I was then going to ask what is the intent of the code originally, then donphillips posted before I could ask the question.

So STARS FOR EVERYONE!
 