crb7
Mechanical
- Jul 4, 2018
- 47
hi guys;
I have a petroleum factory which is stored flammable liquids in tanks. There is a table in NPFA10 that tell us the fire extinguisher size and placement for class B fire.
But also there is paragraph which is said:
6.3.2.3 For flammable liquid hazards of appreciable depth, a
Class B fire extinguisher shall be provided on the basis of at
least 2 numerical units of Class B extinguishing potential per
1 ft2 (0.09 m2) of flammable liquid surface of the largest hazard area.
1.May you tell me what does it mean by "flammable liquid hazards of appreciable depth"?
2.Shall I use the above table or 6.3.2.3 sentence?
3.When Shall we use wheeled fire extinguishers?
I have a petroleum factory which is stored flammable liquids in tanks. There is a table in NPFA10 that tell us the fire extinguisher size and placement for class B fire.
But also there is paragraph which is said:
6.3.2.3 For flammable liquid hazards of appreciable depth, a
Class B fire extinguisher shall be provided on the basis of at
least 2 numerical units of Class B extinguishing potential per
1 ft2 (0.09 m2) of flammable liquid surface of the largest hazard area.
1.May you tell me what does it mean by "flammable liquid hazards of appreciable depth"?
2.Shall I use the above table or 6.3.2.3 sentence?
3.When Shall we use wheeled fire extinguishers?