Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Fire Hydrant Testing - Help

Status
Not open for further replies.

FireFreak08

Mechanical
Oct 31, 2008
20
I have a project where a flow test was done. The test hydrant was located on a "Street A" nearest the to the incoming service to the building and the flow hydrant was on "Street B" which runs perpendicular to "Street A".

At the end of the project, the incoming service needed to flip. It went from Street A to Street B. My question is, does it matter as far as flow testing is concerned. I learned by the phrase "flow past the test hydrant". In the original test, this is true. However the new layout, the flow hydrant is now closest to the incoming water service. Would this make a difference hydraulically?

I happen to think it would but I could be wrong. Street B could have a smaller main, could have different feeds. I don't really know because the site plan doesn't indicate it.

Also, is there a code/standard that states how often hydrants should be tested?
 
Replies continue below

Recommended for you

I think you answered your own question. I can't offer an accurate answer without a more thorough survey of the H2O supply system and more information such as elevation changes, gravity or pumped, etc.

The standarad you are looking for is actually a recommended practice: NFPA 291.
 
Sounds like a new flow test needs to be done, just to check
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor