ellen messer
Mechanical
- Mar 14, 2018
- 1
I have a 75 hp fire pump that is fed from the utility tranformer and the emergency switchgear. The emergency switchgear has a 600amp breaker in the gear for the fire pump in the event of a lose of normal power. It is my understanding that per NEC,the size of the breaker and conductor must be sized 123% higher than the actual fire pump ampherage. Meaning the minimum size of the breaker and conductor would be 125 AMP. I have been told, just cant find it, that NEC also says no higher than 250% which would mean a 250amp breaker.
the engineer has directed us to install the 600amp breaker but to use a conductor for 125amp.
is it true NEC has a max? and is the engineer asking us to install a system that doesnt meet code?
please advise
ellen
the engineer has directed us to install the 600amp breaker but to use a conductor for 125amp.
is it true NEC has a max? and is the engineer asking us to install a system that doesnt meet code?
please advise
ellen