I have a fire pump and since the GC was going to pour more concrete, we set the pump up on 3/4" A. T. Rod with 1" sch 80 pipe nipples (sleeved the Rod) and they formed and poured the pump pad, my question is; the lower lip of the pump base is encased in the concrete so where does the NFPA 20 requirement come into play for grouting?

spkreng, CET
 
Replies continue below

Recommended for you

If I recalled correctly I had the same question while taking a NICET test.
The answer I found was that the entire based must be in contact with the concrete and the entire based must be filled with concrete as well. No empty pockets allowed.
 
I agree with NJ1. The last ten pumps I installed, the pad was formed all the way up to the bottom of the base plate which would fulfill your grouting requirement.