Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Fire pump room requirements 4

Status
Not open for further replies.

chaz12

Mechanical
Jan 8, 2007
12
Does NFPA 20 require that the pump room be dedicated exclusively to the fire pump equipment? Due to space limitations, we wanted to have a pump room that would contain the hot water and chilled water pumps along with the fire pump. The room is 2 hour rated and will be sprinkled.

Thanks

Chaz
 
Replies continue below

Recommended for you

where are you sticking this??? high rise, warehouse, one story office building????????
 
NFPA 20, 2007 A5.12.1.1.1 As long as the equipment does not pose a fire hazard, i.e. a boiler, it is OK.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor