Fire pump room ventilation

Status
Not open for further replies.

emalsyd

Mechanical
Joined
May 10, 2006
Messages
43
Location
US
Does a fire pump room with an electric fire pump require ventilation. I can find ventilation requirements if using a diesel or gas powered fire pump but can't find anything for an electric fire pump. I wouldn't think any would be required since there is no combustion happening.
 
There isn't, but that big ol' motor will generate some serious heat. Doesn't hurt to have a small louver and exhaust fan (careful of placement don't freeze your pipe!)
 
There may not be any combustion happening, but there will be heat generation, so yes. Since you don't have the combustion of a diesel pump, it is more like a typical mechanical room in terms of ventilation requirements.
 
NFPA 20 4.12.6 Ventilation.
Provision shall be made for ventilation of a pump room or pump house.
 
If in the middle east, calculate ventilation air flow rate for max temperature rise of 5degC
 