I have a newer four story office building where the fire pump has not been set up as per 20 / A.14.2.7. I have noted this in inspection reports and the client has asked me to clarify. Currently the jockey pump is set to 100 / 130 and the fire pump is set to 85 / 95.
Fire pump specs out at 100 psi / 500 gpm with a 110.8 psi churn. Minimum static suction supply has been recorded at 60 psi with a maximum of 85 psi.
According to A.14.2.7 the settings should be:
Jockey pump stop: 110 + 60 = 170 psi
Jockey pump start: 170 – 10 = 160 psi
Fire Pump stop: 110 + 60 = 170 psi
Fire Pump start: 160 – 5 = 155 psi
The fire pump churn with max city supply would be in the 195 psi range. Presumably then, if the system is solid, system pressures would stay at about this pressure, with the weekly 10 minute runs.
This seems like a rather high 'normal' pressure. Am I missing something here / have my figures wrong? Due to the presence of a standpipe system, prv’s or restriction devices would be required on the 2 ½” valves? Are there other implications I may be missing?
Thx
Fire pump specs out at 100 psi / 500 gpm with a 110.8 psi churn. Minimum static suction supply has been recorded at 60 psi with a maximum of 85 psi.
According to A.14.2.7 the settings should be:
Jockey pump stop: 110 + 60 = 170 psi
Jockey pump start: 170 – 10 = 160 psi
Fire Pump stop: 110 + 60 = 170 psi
Fire Pump start: 160 – 5 = 155 psi
The fire pump churn with max city supply would be in the 195 psi range. Presumably then, if the system is solid, system pressures would stay at about this pressure, with the weekly 10 minute runs.
This seems like a rather high 'normal' pressure. Am I missing something here / have my figures wrong? Due to the presence of a standpipe system, prv’s or restriction devices would be required on the 2 ½” valves? Are there other implications I may be missing?