Fire rated ceiling and dampers?
John_187
68
There is an elevator machine room on this project. It has fire rated walls and fire rated ceiling. There are 2 exhaust grilles in the fire rated ceiling. These exhaust grilles then combine into a single duct that passes through the fire rated wall. The duct passing through the fire rated wall has a fire damper. But do the two exhaust grilles require a fire damper as well?
I was starting to look for a code that might say, haven't found anything so far.
Please provide any input if you know about this situation, thanks
Are they "exhaust" or "return"? Pretty sure "exhaust" is not allowed to have dampers at all.
If they are "return" air, then the grilles wouldn't need dampers if there is a fire damper in the rated wall.
I'd also be asking the architect why the ceiling is rated? What floor is the machine room on? (Why is there even a ceiling?)
Not sure what state you are in, but in the mechanical code, exhaust chapter, you can find which systems are not allowed to have fire dampers installed - clothes dryers, hazardous exhaust, kitchen exhaust, maybe a few others. Any general exhaust can have a fire damper just like a supply or return gets one.
If it doesn't create a more dangerous situation by having a damper close in a fire event, you should put in the damper. So if this is exhaust a machine room just to cool it, and there isn't anything hazardous within the room, you likely should have a damper.
As far as the rated ceiling vs wall, it's unclear why a ceiling would be rated, if the walls surrounding the room are rated as well. But if both are rated, both probably need a damper. Unless the duct meets some of the exceptions to not require a damper, which depending on the wall type is possible if ducts are all steel of a certain thickness, and under a certain duct size, fully sprinklered, etc.
Better put the fire dampers in. This will avoid a change order later.