Fire retardant vs. fire resistant cables

Status
Not open for further replies.

Power0020

Electrical
Jun 11, 2014
303
I understand that flame retardant cables don't have capability to continue in operation during a fire, while fire resistant cables can operate during fires for certain time.

most of power plants require LV & MV cables to be flame retardant where I may think that flame resistance cables may be required for vital circuits. I couldn't find any recommendation in NEC.

Any clue?
 
Replies continue below

Recommended for you

NEC Art. 700.10 Wiring, Emergency System. (D) Fire Protection.
Feeder-Circuit Wiring.
Feeder-circuit wiring shall meet one of the following conditions:
(2) Be a listed electrical circuit protective system with a minimum 2-hour fire rating.
ARTICLE 728: Fire Resistive Cable Systems
An information note recommends UL 2196-2006, Standard for Tests of Fire Resistive Cables.
See also-for instance-: