jdelahunt
Specifier/Regulator
- Jun 11, 2012
- 1
All;
As an AHJ/Owner's Rep, we get called to accept new sprinkler installations. From time to time, we have installers that will fill the new system, then immediately pump the system up to 200+ psi, and allow the water to heat up in the South Texas sun. At the end of the two hour test, our pressure has risen (both due to the coefficient of expansion of the water and the dissolution of air due to increased temperature).
We can't tell from a pressure rise whether there are no leaks - the system might have a bleeder that lets 2 psi off, but the system temp creates a 7 psi gain, or it might be tight and the system temp has created a 5 psi gain. Since we can't tell, we reject the test. However, the result is "no pressure loss," which meets the letter of the code.
We prefer that they allow the water to temper for 24+ hours, but this doesn't always happen.
We can model temperature effect on pneumatic systems pretty well by applying PV=nRT, but hydrostaic testing is a little more finicky. How do you, my fellow AHJs, react to pressure gains on hydrostatic tests?
As an AHJ/Owner's Rep, we get called to accept new sprinkler installations. From time to time, we have installers that will fill the new system, then immediately pump the system up to 200+ psi, and allow the water to heat up in the South Texas sun. At the end of the two hour test, our pressure has risen (both due to the coefficient of expansion of the water and the dissolution of air due to increased temperature).
We can't tell from a pressure rise whether there are no leaks - the system might have a bleeder that lets 2 psi off, but the system temp creates a 7 psi gain, or it might be tight and the system temp has created a 5 psi gain. Since we can't tell, we reject the test. However, the result is "no pressure loss," which meets the letter of the code.
We prefer that they allow the water to temper for 24+ hours, but this doesn't always happen.
We can model temperature effect on pneumatic systems pretty well by applying PV=nRT, but hydrostaic testing is a little more finicky. How do you, my fellow AHJs, react to pressure gains on hydrostatic tests?