Hi all,
I hope someone out there could help me with this problem. We have an offshore installation with a total of 5 fire water pumps supplying the ring main. System is pressurized with a single jockey pump. Max total deluge load in a single fire zone requires two pumps to start up to meet demand.
Start-up time for the pumps is around 15-20 seconds, deluge valve open in a much shorter time span upon F&G detection. What happens is that the pump start-up sequence is initiated, the two pumps start to rev up, and then we loose total ring main pressure because deluge valve goes fully open before the two pumps reach full capacity. Naturally the jockey pump cannot compensate for the shortfall (nor is it meant to do so.)
This causes PSLLs on all fire water pumps to start EVERY fire water pump on the facility, which is safe, but a waste of resources, especially when we are just conducting regular testing of the system. In addition, we get pressure surges in the system, which has caused pipe ruptures in the system (GRP). The latter is probably due to poor design, and is being rectified.
Now my question is this: Would it be acceptable to either delay the opening of the deluge valve until the pumps have reached full capacity, alternatively increasing the opening time so that flow through the valve will not exceed the pump output at any time?
Appreciate any comments or suggestions you guys or girls may have on the subject.
I hope someone out there could help me with this problem. We have an offshore installation with a total of 5 fire water pumps supplying the ring main. System is pressurized with a single jockey pump. Max total deluge load in a single fire zone requires two pumps to start up to meet demand.
Start-up time for the pumps is around 15-20 seconds, deluge valve open in a much shorter time span upon F&G detection. What happens is that the pump start-up sequence is initiated, the two pumps start to rev up, and then we loose total ring main pressure because deluge valve goes fully open before the two pumps reach full capacity. Naturally the jockey pump cannot compensate for the shortfall (nor is it meant to do so.)
This causes PSLLs on all fire water pumps to start EVERY fire water pump on the facility, which is safe, but a waste of resources, especially when we are just conducting regular testing of the system. In addition, we get pressure surges in the system, which has caused pipe ruptures in the system (GRP). The latter is probably due to poor design, and is being rectified.
Now my question is this: Would it be acceptable to either delay the opening of the deluge valve until the pumps have reached full capacity, alternatively increasing the opening time so that flow through the valve will not exceed the pump output at any time?
Appreciate any comments or suggestions you guys or girls may have on the subject.