Cryodude

Computer
Jan 27, 2005
5
Can one calculate FLA or is that just a function of operation. In other words the pump is designed with design criteria being
Torque Speed / Eff and you get what you get within reason. Or is there a specific calculation.
 
Replies continue below

Recommended for you

You may be able to calculate the Brake Horse Power (BHP) that you need at the pump, and from that the Running Load Amps (RLA). However motors only come in specific sizes. So after determining the BHP, you select the next size motor that is equal to or greater than the requirement, and then that motor has a FLA rating. From the standpoint of electrical circuit design that is the number you must work with.