Flame rods or ionization probes fail?

Status
Not open for further replies.

Neosec

Electrical
Mar 28, 2012
3
0
0
US
I read a post by op9 regarding the theory of operation of Flame rods or ionization probes from back in July of 2007 - which was very informative. My question is, can a flame rods or ionization probes go bad? Are there any active parts in them that fail? My understanding is that these are simply a metal rod usually Kanthal (iron-chromium-aluminium). Am I correct that a build-up of foreign deposits that would reduce conductivity could be cleaned off with emery cloth? Other than that failures would be physical. Failure of the insulation required for mounting or failure of the terminal connection for the electrical wire. Right? I was speaking with an HVAC guy that said they do go bad... I wondered, how do they go bad?
Thanks in advance.

Chuck
 
Replies continue below

Recommended for you

Loss of insulation between the rod and "ground" is probably the most common failure mode.

This can occur from soot build-up on the insulator, or from various cleaning fluids or other liquids wicking in between the rod and insulator.

 
A couple other failure modes:

AC excitation supply voltage too low

Condensed moisture on flame rod when cold reduces area, signal too low

Rich, yellow flame is insufficently conductive, DC current too low

Flame rod made from coat hanger wire, brake tubing or welding rod will tend to fail is much shorter time than one made of Kanthal.
 